Bench setup, looks like this:
![Image](https://lh4.googleusercontent.com/-0d3Vtu_sJo8/VHtr3WdfC6I/AAAAAAAALAo/Wcv_qZaonVE/s800/WP_20141130_10_32_17_Pro.jpg)
In the first part of the log, the cal points are 20 psi/.489V and 480 psi/ 3.951V. It gives good values when I apply shop air pressure to the sensor, but about 20 psi low. When I put in the actual sensor calibration values, line pressure is erratic at zero applied pressure. When I apply 100psi, it settles down and line pressure = applied pressure.
Is line pressure gauge or absolute? Should I not use 0psi as a cal point?